A fully loaded 6513 would put out? I need this so I can properly upgrade a data center's air Conditioning.
Solved! Go to Solution.
03-23-2005 08:01 AM
03-23-2005 08:01 AM
03-23-2005 08:34 AM
Thanks. That was what I needed.
04-02-2005 06:17 AM
You can also calculate Watts->BTUs with the following formulas:
For Watts --> BTU/Hour, multiply the wattage by 3.413
For Watts --> BTU / Minute, multiply the wattage by .005689
You can get a rough value for watts by multiplying the voltage X the amperage (i.e., 120V @ 10Amps = 1200 Watts .... not exactly, but close enough).
FWIW
Scott
06-01-2005 03:31 AM
Ciscos also have a tool to work out the exact power and heat load based on actual configuration. Also provides the % of capacity utilised on the power supplies units, pretty essential at design phase to ensure the correct PSUs are specified.
A must use tool.....