10-15-2021 05:12 AM
Hello,
Is it possible to use C9200 and C9300 in a 15U rack in a server room without air conditioner ?
Thanks,
HM
Solved! Go to Solution.
10-18-2021 01:39 AM
I do know many of them used with the RISK, and failure domain was high and you need to replace depends on business you looking to deploy.
You need to consider your risk vs availabliyt to deployment of the devices, if that is the requirement need to look for right choice of models.
If those works as expected in the head, why do they have industrial switches ?
10-15-2021 05:36 AM
Look at below :
10-15-2021 05:47 PM
@mtmharison wrote:
Is it possible to use C9200 and C9300 in a 15U rack in a server room without air conditioner ?
Not enough info:
1. How many switches in a rack?
2. How many power supplies installed (per switch) per rack?
3. How "big" are the power supplies?
4. Does the rack have free airflow?
5. Obstruction(s) to 5 sides of the rack?
6. Dust condition inside and outside of the rack?
7. What is the exact model of the switches?
8. Other than the switch/switches, what other equipment are found inside the rack?
10-18-2021 12:44 AM
But has anyone ever used these kind of switches without any air conditioning system?
10-18-2021 01:39 AM
I do know many of them used with the RISK, and failure domain was high and you need to replace depends on business you looking to deploy.
You need to consider your risk vs availabliyt to deployment of the devices, if that is the requirement need to look for right choice of models.
If those works as expected in the head, why do they have industrial switches ?