06-09-2013 08:09 PM - edited 03-07-2019 01:47 PM
Hi,
The fans 1 & 2 in Module 1 on the Nexus5K are still experiencing the very high RPM and speed issue.
I have replaced the fan from another operational Nexus5K, and the fans are fine in the other Nexus. The replacement fans also have the same issues, so it is not a fan hardware issue.
There are no threshold alarms. the only log entry that is related to this is as follows:
%NOHMS-2-NOHMS_ENV_ERR_FAN_SPEED: System minor alarm in fan tray 1: fan speed is out of range on fan 1. 7950 to 12500 rpm expected.
I have provided the output for both the fan detail and the temperature.
N5K-01# sh environment fan detail
Fan:
---------------------------------------------------
Module Fan Airflow Speed(%) Speed(RPM)
Direction
---------------------------------------------------
1 1 Back-to-Front 60 13881
1 2 Back-to-Front 60 12705
2 1 Back-to-Front 60 8463
2 2 Back-to-Front 60 8477
3 1 Back-to-Front 60 8477
3 2 Back-to-Front 60 8450
4 1 Back-to-Front 60 8385
4 2 Back-to-Front 60 8626
Power Supply:
-----------------------------------
Module Airflow Configured
Direction Speed (%)
-----------------------------------
1 Back-to-Front 100
2 Back-to-Front 100
Temperature
-----------------------------------------------------------------
Module Sensor MajorThresh MinorThres CurTemp Status
(Celsius) (Celsius) (Celsius)
-----------------------------------------------------------------
1 Outlet 65 55 36 ok
1 PS-1 63 60 30 ok
1 PS-2 63 60 31 ok
Please let me know what can be done. Is that speed within acceptable limit.
Thanks
Nachi
Solved! Go to Solution.
06-09-2013 09:05 PM
Usually this error message means that your have fan tray fault.
Is the same fan tray working fine on the other nexus?
Can you try reseating it again? Once you done provide me the following outputs:
show env fan
show en power in
show logging last 100
Regards
Inayath
06-09-2013 09:05 PM
Usually this error message means that your have fan tray fault.
Is the same fan tray working fine on the other nexus?
Can you try reseating it again? Once you done provide me the following outputs:
show env fan
show en power in
show logging last 100
Regards
Inayath
06-09-2013 09:16 PM
Yes, the fan tray works fine on the other nexus switch.
06-09-2013 09:23 PM
output of requested commands plz?
06-09-2013 11:08 PM
Thanks Inayathulla. Cisco confirmed that's a faulty hardware and sending a replacement.
12-01-2014 11:27 AM
hi nachi,ece,
please advise what hardware was replaced, i.e. fan trays or entire chassis etc.
i have a client with exactly the same situation.
thanks.
any additional advise would be appreciated.
12-01-2014 04:58 PM
Hi Francois,
Replaced the whole switch.
Thanks