Dear friends, one nexus 7010 10G Ethernet module (N7K-F132XP-15) is not working. It was working till yesterday. After that it went down.
I checked by #show module, It's power was down. I executed the command #no poweroff module 3 and reload that module by command reload module 3. It's power came up but status is not OK but powered-up. I reloaded the switch but status is same.
So please help to resolve the issue. Below is the output of show module.
N7K-1#
N7K-1# show module
Mod Ports Module-Type Model Status
--- ----- ----------------------------------- ------------------ ----------
1 48 10/100/1000 Mbps Ethernet Module N7K-M148GT-11 ok
2 8 10 Gbps Ethernet XL Module N7K-M108X2-12L ok
3 32 1/10 Gbps Ethernet Module N7K-F132XP-15 powered-up
5 0 Supervisor module-1X N7K-SUP1 active *
Mod Sw Hw
--- -------------- ------
1 5.2(9a) 1.7
2 5.2(9a) 1.2
3 NA 1.3
5 5.2(9a) 2.0
Thanks
Mod MAC-Address(es) Serial-Num
--- -------------------------------------- ----------
1 00-07-7d-5d-eb-10 to 00-07-7d-5d-eb-44 JAFXXXXXXX1
2 e8-b7-48-fd-22-24 to e8-b7-48-fd-22-30 JAFXXXXXXX2
3 e8-b7-48-1f-3d-f4 to e8-b7-48-1f-3e-38 JAFXXXXXXX3
5 40-55-39-23-ab-b0 to 40-55-39-23-ab-b8 JAFXXXXXXX4
Mod Online Diag Status
--- ------------------
1 Pass
2 Pass
3 Untested
5 Pass
Xbar Ports Module-Type Model Status
--- ----- ----------------------------------- ------------------ ----------
1 0 Fabric Module 1 N7K-C7010-FAB-1 ok
2 0 Fabric Module 1 N7K-C7010-FAB-1 ok
3 0 Fabric Module 1 N7K-C7010-FAB-1 ok
Xbar Sw Hw
--- -------------- ------
1 NA 1.1
2 NA 1.1
3 NA 1.1
Xbar MAC-Address(es) Serial-Num
--- -------------------------------------- ----------
1 NA JAFXXXXXXX1
2 NA JAFXXXXXXX2
3 NA JAFXXXXXXX3
* this terminal session
N7K-1#
N7K-1#
N7K-1#
N7K-1# sh environment power
Power Supply:
Voltage: 50 Volts
Power Actual Total
Supply Model Output Capacity Status
(Watts ) (Watts )
------- ------------------- ----------- ----------- --------------
1 N7K-AC-6.0KW 664 W 6000 W Ok
2 N7K-AC-6.0KW 657 W 6000 W Ok
3 ------------ 0 W 0 W Absent
Actual Power
Module Model Draw Allocated Status
(Watts ) (Watts )
------- ------------------- ----------- ----------- --------------
1 N7K-M148GT-11 N/A 400 W Powered-Up
2 N7K-M108X2-12L 475 W 650 W Powered-Up
3 N7K-F132XP-15 N/A 385 W Powered-Up
5 N7K-SUP1 N/A 210 W Powered-Up
6 supervisor N/A 210 W Absent
Xb1 N7K-C7010-FAB-1 N/A 60 W Powered-Up
Xb2 N7K-C7010-FAB-1 N/A 60 W Powered-Up
Xb3 N7K-C7010-FAB-1 N/A 60 W Powered-Up
Xb4 xbar N/A 60 W Absent
Xb5 xbar N/A 60 W Absent
fan1 N7K-C7010-FAN-S 76 W 720 W Powered-Up
fan2 N7K-C7010-FAN-S 76 W 720 W Powered-Up
fan3 N7K-C7010-FAN-F 8 W 120 W Powered-Up
fan4 N7K-C7010-FAN-F 8 W 120 W Powered-Up
N/A - Per module power not available
Power Usage Summary:
--------------------
Power Supply redundancy mode (configured) PS-Redundant
Power Supply redundancy mode (operational) PS-Redundant
Total Power Capacity (based on configured mode) 6000 W
Total Power of all Inputs (cumulative) 12000 W
Total Power Output (actual draw) 1321 W
Total Power Allocated (budget) 3835 W
Total Power Available for additional modules 2165 W
N7K-1#
N7K-1#
N7K-1#