VLANs accidentally removed from trunk on Nexus 7K
aweise
We have two Nexus 7706 switches in our data center. Both are running 8.2(1).
This morning, I went to remove a specific VLAN from a port-profile. This port-profile is tied to several VPC port-channel interfaces (shared across both 7Ks), which are trunks to our ESX servers. The configuration is like so:
port-profile type port-channel ESX
switchport
switchport mode trunk
switchport trunk native vlan 999
switchport trunk allowed vlan 130-132,134-158,164-170,174,177-178,181
switchport trunk allowed vlan add 183-184,190,321,401,552,652,1000
spanning-tree port type edge trunk
speed 10000
duplex full
description ESX Server
state enabled
I ran this command: on both 7Ks:
Switch(config)#port-profile type port-channel ESX
Switch((config-port-prof)#switchport trunk allowed vlan remove 140
A few minutes later, we realized some systems were down. Ultimately, I found that the port-profile configuration had removed several VLANs:
switchport
switchport trunk allowed vlan 130-132,134-139,141-158,164-170,174,177-178,181
speed 10000
duplex full
I have a TAC case open to investigate this, but has anyone else come across this?
balaji.bandi
Not sure what happens on the background :
if the profile apply as below :
switchport trunk allowed vlan add 183-184,190,321,401,552,652,1000   -  << above command overide this.
as per your command :
switchport trunk allowed vlan 130-132,134-139,141-158,164-170,174,177-178,181  ( VLAN 140 removed here and profile applied,)
switchport trunk allowed vlan  - when you use this command what ever configuration on the interface  will be wiped and new allowed VLAN added.
so make sure you profile has full vlan like as below  example :
switchport trunk allowed vlan 130-132,134-158,164-170,174,177-178,181, 183-184,190,321,401,552,652,1000
BB
How would the one command override the other?
When I initially applied the configuration, I did so as you suggested:
switchport trunk allowed vlan 130-132,134-158,164-170,174,177-178,181183-184,190,321,401,552,652,1000
When I display the running config, it's shown in the two-line format, with the second line using the "add" command. Thus, nothing should be overriding any other command.
When I did the remove of a single VLAN ID, the second line somehow got removed from the config. So, the switch updated the port profile to remove VLAN 140, but it also removed the second line with all of those VLANs.
I've removed VLANs numerous times before from these port profiles and have never seen this happen.
Technically as soon the command issued - switchport trunk allowed vlan  all other config removed from port-channel.
I have not worked on the profile, let me read (if any clarification let you know)
In the Future you do not like this happens, make sure you update the profile as suggested.
BB
Yes, I understand that, but that's not how the configuration was applied.
When I first set up the port profile, I used this command:
switchport trunk allowed vlan 130-132,134-158,164-170,174,177-178,181,183-184,190,321,401,552,652,1000
After that, doing a "show run port-profile" on the Nexus displays it like this:
I did not execute the general "switchport trunk allowed vlan" command. I did the following:
Please note that I used the "remove" keyword so that I would only remove vlan 140 from the trunk configuration and not anything else.
It was after this command that I found the second line of the port-profile missing.