cant acknowledge some faults

gdesmo123
Level 1
Level 1

Fw 2.0 3c I have several major "link down's" & "bmc-pre-config-pnuoslocal-failed" - where acknowledge fault is greyed out. There are many other major events I can acknowledge and clear though.

 

Thanks

 

 

 


 <faultInst
 ack="yes"
 cause="link-down"
 changeSet=""
 
 code="F0283"
 created="2014-01-06T13:03:11"
 descr="ether VIF N/A / 1 A-1888 down, reason: Non participating"
 dn="sys/rack-unit-1/fabric-A/path-1/vc-1888/fault-F0283"
 highestSeverity="major"
 id="1208592"
 lastTransition="2014-01-06T13:03:11"
 lc=""
 occur="1"
 origSeverity="major"
 prevSeverity="major"
 
 rule="dcx-vc-down"
 severity="major"
 status="created"
 tags="network,server"
 type="network">
 </faultInst>

 


 <faultInst
 ack="yes"
 cause="bmc-pre-config-pnuoslocal-failed"
 changeSet=""
 
 code="F0367"
 created="2014-06-23T02:45:43"
 descr="No link between IOM port 4/2/2 and fabric interconnect B:1/8"
 dn="sys/chassis-4/slot-2/fabric/port-2/fault-F0367"
 highestSeverity="major"
 id="591419"
 lastTransition="2014-06-23T02:45:43"
 lc=""
 occur="1"
 origSeverity="major"
 prevSeverity="major"
 
 rule="ether-switch-intfio-satellite-connection-absent"
 severity="major"
 status="created"
 tags="network"
 type="connectivity">
 </faultInst>

 

 

3 Replies 3

Keny Perez
Level 8
Level 8

Hello,

The first error message you reported is usually cause by the reasons I describe here, did you check that already?

https://supportforums.cisco.com/discussion/12072961/vif-bound-physcial-interface-down

Second error message, did you check the port 1/8 on FI-B already, to be sure the cable is properly connected?, to see if the port is enabled in the FI?  Did you check if there are CRC errors or changed the cable? or did you confirm the IOM is 100% healthy? 

 

If the Acknowledge Fault button is grayed, it means that it was acknowledge already, but if the alert does not go away it means that even after the alert was ascked, the condition is still taking place.

 

-Kenny

 

The first one was related to that url and a nic being disabled within windows.

 

Fi port 1/8 looks fine and the io module is in an operable status. But the fabric port 2/2 is in an overall status of "up" and acknowledged. But the discovery is "absent" instead of "present" as on other fabric ports without the faults.

 

Does a re-ack of chassis or reset of the io module need to be done to clear fault?

 

Thanks

 

Both, reack of chassis and IOM reseat (not reset) may work, just see what is less disruptive... However, I would still look for a possible bad SFP/cable. Have you checked the port's LED status physically? I mean is it solid green/amber?

 

-Kenny

Review Cisco Networking for a $25 gift card