05-07-2020 01:57 PM
Hello all,
Is it possible to run a C220 M5 server with one power supply plugged into 220V and the other power supply plugged into 110V at the same time?
Appreciate any response,
Ron
Solved! Go to Solution.
05-08-2020 04:04 AM - edited 05-08-2020 04:26 AM
Greetings.
This is not the intended configuration, and is definitely not supported for extended use.
I suspect which ever PSU comes online first will set the expected voltage levels.
I think this will cause issues for the power backplane that is handling power load balancing and redundancy, and is expecting symmetrical sources.
While this might 'work' , you would be plagued with never ending alerts and errors from the CIMC for the PSUs.
You also typically get less wattage output from the PSUs in 110 mode.
You are welcome to put in a TAC case and pose that question, for which TAC would probably reach out to the Product managers for a more formal response.
Kirk...
05-07-2020 02:07 PM
its really odd requirement, what is the use case here.. people have either 220 or 110, i have seen the requirement convert 220 to 110 volts and use it due to PSU purchaed 110V one.
05-07-2020 02:17 PM
One PDU is conncetd to a 220V electric network and the other PDU is connected to a 110V electric network. This is a live environment and I need to make sure that this kind of configuration is supported.
05-07-2020 02:27 PM
As per my understand and document, depends on the PSU you purchased and installed. (high level i do not believe it support, until you purchased 2 different PSU and installed in it).
05-07-2020 02:41 PM
Thank you for the link however the article only says what kind of Voltage you can use with you power supply, it does not say if mixing a 220V and a 110V is supported.
770W & 1050W AC Input Voltage - Nominal range: 100–120 VAC, 200–240 VAC
1600W AC Input Voltage - Nominal range: 200–240 VAC
I'm using the 1050W one, so both can work for me but can they work together?
05-08-2020 04:04 AM - edited 05-08-2020 04:26 AM
Greetings.
This is not the intended configuration, and is definitely not supported for extended use.
I suspect which ever PSU comes online first will set the expected voltage levels.
I think this will cause issues for the power backplane that is handling power load balancing and redundancy, and is expecting symmetrical sources.
While this might 'work' , you would be plagued with never ending alerts and errors from the CIMC for the PSUs.
You also typically get less wattage output from the PSUs in 110 mode.
You are welcome to put in a TAC case and pose that question, for which TAC would probably reach out to the Product managers for a more formal response.
Kirk...
05-08-2020 04:13 AM
Thank you very much