09-13-2010 04:25 AM - edited 03-01-2019 09:42 AM
Hi All
I have just installed a pair of UCS C210 M1 servers for Unified Communications Manager, however one of the servers is very noisy and does not seem to want to quiet down, the other server is fine, I have checked inside and all fans are running and is cool. Does anyone know what I could check to make sure this is running correctly.
Initially when I had these in the lab they went quiet after about an hour, however now on customer site one doesn't seem top want to do so and this.
Regards
Nick
09-14-2010 05:01 AM
Nick,
login to the CIMC, on the left side highlight Summary check the server status in the center of the page in the right hand pane. You should see an over all status of Good.
In the left pane highlight sensors, in the right pane there are tabs for Power Supply, Fan, Temperature, Voltage and Current Sensors. Check all of these to ensure no thresholds have been crossed.
In the left pane highlight System Event Log on the right pane scroll through the messages to see if you have any entries that may be related such as critical fan alarms, power supply alarms.
If any alarms are present, a power supply, fans etc could be replaced. If this all checks out then the Server is running properly, if however you still feel uncomfortable due to the noise you could always opt for an RMA by opening a TAC Service Request.
If you are not familiar with or have not setup CIMC as of yet I have enclosed a link if you look at the bottom of the page under C200 M1 you will
see links to documentation regarding how to set up CIMC as well as troubleshooting tips.
http://www.cisco.com/en/US/products/ps10493/prod_configuration_examples_list.html
Bill
09-14-2010 05:51 AM
Hi Bill
Thanks for your reply, i have checked the CIMC and all appears to be fine, I have checked the system event log and their are no critical errors relating to fans or power supplies so I guess it must be good, will consider an RMA if the customer complains.
Many thanks
Nick
09-14-2010 02:59 PM
Nicholas,
Can you check the fan speeed from the CIMC. Let me know what the value is (RPMs).
I have seen the case where the fans were spinning high, and pulling & reseating the Power Supplies (one at a time) fixed the issue.
Robert
09-15-2010 04:59 AM
09-15-2010 06:18 AM
Nick,
Take a look at CSCth30950 it is related to high fan speed due to the algorithm miscalculating the fan speed.
This bug is related to CIMC version 1.1 or lower. The workaround as mentioned by Robert is to reseat the
power supplies. The CIMC firmware that contains the fix for this is not available as of yet and we have no
firm ETA on a release date. The fan speeds that I see in the lab are running psu 2400 - 2500
fans 5400 - 5600.
Thanks,
Bill
Discover and save your favorite ideas. Come back to expert answers, step-by-step guides, recent topics, and more.
New here? Get started with these tips. How to use Community New member guide