Nexus Fail over
galaga
New to Nexus, we have a Nexus 56128P, we experienced Cisco Bug: CSCus68610
https://quickview.cloudapps.cisco.com/quickview/bug/CSCus68610
During this our fail over did not work since the device was hung. Is there a way to set up the fail over/vpc to fail over if an IP is not reachable or if there is an internal failure  ?
The fix for bug CSCus68610 was incomplete and does not address all conditions for this issue.)
A Nexus 5672 or Nexus 56128 may hang or reset with unknown reason
From the "show logging onboard internal reset-reason",
 Reset Reason (HW): uC reset code: 0x4800 <<<<
OR
 Reset Reason (HW): uC reset code: 0x400b
Prior to reset/hang, syslog messages such as following can be displayed (if the code version is above 6.0(2)N2(5) or 7.0(3)N1(1))
Conditions:
Correctable errors seen on the internal PCIE bus.
Workaround:
Refer to the following field notice to obtain fix for this issue
http://www.cisco.com/c/en/us/support/docs/field-notices/641/fn64110.html
18 Replies 18
ADP_89
Hello Galaga,
There is no way to failover the entire VPC peer as VPC is an active-active technology. If all of your interfaces are VPC port-channel you could use lacp fast timers in order to have the connected devices noticing the problem faster. Generally these are corner case that Cisco fixes with software, like in your case.
HTH,
ADP
Could you elaborate on  lacp fast timers  ?
We have a WAN router from a vendor for internet access, is there a way to monitor that IP, if that IP is not reachable, then fail over ?
When this happened we lost access to everything behind the MPLS (our LAN)
How to tie this into VCP ? or use timers ? The vendor WAN router only has (1) physical interface, I believe......
You may want to enable vPC object tracking. You can go through the following cisco live session for details on vPC
https://www.ciscolive.com/global/on-demand-library/?search=vpc#/session/14479207929320017eHp
With object tracking, I could add a non Nexus device (Cisco 3900 Router) via IP address, and if that IP is not reachable, SW1 goes to SW2  ? See attached PDF
Thanks for your input
Normally LACP ports will drop out from a Port-Channel once they do not receive LACP packets for 90 seconds (basically 3 miss LACPDU as they are sent every 30seconds). Fast rate LACP are sent instead every 1 second, and eventually the port will be deactivated after 3 seconds. So they will help you only if the devices connected to the Nexus are in a Port-Channel. If your router is connected to you LAN only via a single interface you will not achieve any improvements.
I am not too sure on what failover you would like to achieve, can you post a simple topology of your network and make a better statement on what you would like to get in a specific condition?
Cheers,
ADP
It appears out management interface was down that may be why vPC did not kick in.
Is there a design improvement to check for VPC/Management interface connectivity ?
Add auto recovery and or object tracking ?
[image: image.png]
For optimal operation of vPC it is recommended to dual-home to all external devices. In your case it would be ideal to dual-home to the vendor switch.
If you cannot dual home to the vendor switch, I would suggest that you connect the link to the ISP using the switch which is vPC primary. Infact all single homed devices should be connected to vPC primary. As vPC secondary switch suspends all its connection if the vPC peer-link between the switches fail.
Also are you running IP routing protocol between the nexus and the vendor switch, if yes, you may have to run the NXOS version 7.3(0)N1(1)
Dynamic routing over vPC or L3 vPC is only supported from this release.
https://www.cisco.com/c/en/us/td/docs/switches/datacenter/nexus5500/sw/release/notes/7x/Nexus5500_Release_Notes_7x.html#pgfId-622079
In our case turns out management interface was down, we experienced Cisco Bug: CSCus68610 on 5K1, which hung. NK2 did not kick in, Rebooting 5K1 resolved the issue.
Everything (our LAN) behind the Vendor WAN router Cisco 3900 was not reachable.
Sorry still learning, homing this is the solution ? Need to add a physical interface on the vendor WAN router to do this ?
I am trying to figure out if we encountered the perfect storm, or we have a design flaw. We should update the IOS, but in the mean time I would like to fix the design flaw.
IOS 7.0(7)
vpc domain 1
role priority 7096
peer-keepalive destination 158.100.1.2 source 158.100.1.1
delay restore 150
interface mgmt0
vrf member management
ip address 158.100.1.1/24
interface port-channel100
description ndcsw0102 (vpc-peer link)
switchport mode trunk
spanning-tree port type network
speed 40000
vpc peer-link
Your WAN router needs to suppor LACP as well so you can team the two interfaces into a Port-Channel. The 2 interfaces will be connected one per Nexus and the configuration will look like the following:
SW1:
interface Ethernet1/5
description TO_MPLS_ROUTER
channel-group 5 mode active
interface Po5
switchport
switchport mode access
switchport access VLAN X
vpc 5
SW2:
interface Po5
switchport
vpc 5
But ideally all your devices should be dual homed to both Nexus.
One more thing, you are saying that NK2 did not kick in, that is not clear. VPC switches are always active active, can you post a "show vpc" from both devices so we can check the status?
ADP
By homing, you mean configuring the WAN as you stated ?
NK2 did not kick in, by say that, I assume if it was working correctly, we would not have had an outage.
By dual homing I mean connecting the device (in your case the 3900) to both Nexus, and configuring the interfaces as I told you earlier.
NK1
Legend:
(*) - local vPC is down, forwarding via vPC peer-link
vPC domain id : 1
Peer status : peer adjacency formed ok
vPC keep-alive status : peer is alive
Configuration consistency status : success
Per-vlan consistency status : success
Type-2 consistency status : success
vPC role : primary, operational secondary
Number of vPCs configured : 592
Peer Gateway : Disabled
Dual-active excluded VLANs : -
Graceful Consistency Check : Enabled
Auto-recovery status : Enabled (timeout = 240 seconds)
vPC Peer-link status
id Port Status Active vlans
1 Po100 up 1,10,20,22,50,100-104,150-154,200-204,206-208,210-
214,300-305,310-313,350-354,400-404,450-454,500-50
4,671,681,690,700-702,707-708,710-711,730-731,800,
997-999,1100
vPC status
id Port Status Consistency Reason Active vlans
101 Po101 up success success -
102 Po102 up success success -
103 Po103 up success success -
104 Po104 up success success -
105 Po105 up success success -
106 Po106 up success success -
107 Po107 up success success -
108 Po108 up success success -
109 Po109 up success success -
110 Po110 up success success -
111 Po111 up success success -
112 Po112 up success success -
102400 Eth101/1/1 up success success 102
102401 Eth101/1/2 up success success 103
102402 Eth101/1/3 down* Not Consistency Check Not -
Applicable Performed
102403 Eth101/1/4 down* Not Consistency Check Not -
102404 Eth101/1/5 down* Not Consistency Check Not -
102405 Eth101/1/6 down* Not Consistency Check Not -
102406 Eth101/1/7 down* Not Consistency Check Not -
102407 Eth101/1/8 down* Not Consistency Check Not -
102408 Eth101/1/9 down* Not Consistency Check Not -
102409 Eth101/1/10 down* Not Consistency Check Not -
102410 Eth101/1/11 down* Not Consistency Check Not -
102411 Eth101/1/12 up success success 102
102412 Eth101/1/13 down* Not Consistency Check Not -
102413 Eth101/1/14 down* Not Consistency Check Not -
102414 Eth101/1/15 down* Not Consistency Check Not -
102415 Eth101/1/16 down* Not Consistency Check Not -
102416 Eth101/1/17 down* Not Consistency Check Not -
102417 Eth101/1/18 down* Not Consistency Check Not -
102418 Eth101/1/19 down* Not Consistency Check Not -
102419 Eth101/1/20 down* Not Consistency Check Not -
102420 Eth101/1/21 down* Not Consistency Check Not -
102421 Eth101/1/22 down* Not Consistency Check Not -
102422 Eth101/1/23 up success success 210
102423 Eth101/1/24 up success success 208
102424 Eth101/1/25 down* Not Consistency Check Not -
102425 Eth101/1/26 down* Not Consistency Check Not -
102426 Eth101/1/27 up success success 100
102427 Eth101/1/28 down* Not Consistency Check Not -
102428 Eth101/1/29 down* Not Consistency Check Not -
102429 Eth101/1/30 down* Not Consistency Check Not -
102430 Eth101/1/31 down* Not Consistency Check Not -
102431 Eth101/1/32 down* Not Consistency Check Not -
102432 Eth101/1/33 down* Not Consistency Check Not -
102433 Eth101/1/34 down* Not Consistency Check Not -
102434 Eth101/1/35 down* Not Consistency Check Not -
102435 Eth101/1/36 up success success 504
102436 Eth101/1/37 down* Not Consistency Check Not -
102437 Eth101/1/38 down* Not Consistency Check Not -
102438 Eth101/1/39 down* Not Consistency Check Not -
102439 Eth101/1/40 down* Not Consistency Check Not -
102441 Eth101/1/42 up success success 102
102444 Eth101/1/45 up success success 310
102445 Eth101/1/46 down* Not Consistency Check Not -
102446 Eth101/1/47 down* Not Consistency Check Not -
102447 Eth101/1/48 down* Not Consistency Check Not -
103424 Eth102/1/1 up success success 102
103425 Eth102/1/2 up success success 103
103426 Eth102/1/3 down* Not Consistency Check Not -
103427 Eth102/1/4 down* Not Consistency Check Not -
103428 Eth102/1/5 down* Not Consistency Check Not -
103429 Eth102/1/6 down* Not Consistency Check Not -
103430 Eth102/1/7 up success success 711
103431 Eth102/1/8 down* Not Consistency Check Not -
103432 Eth102/1/9 up success success 800
103433 Eth102/1/10 down* Not Consistency Check Not -
103434 Eth102/1/11 down* Not Consistency Check Not -
103435 Eth102/1/12 up success success 102
103436 Eth102/1/13 down* Not Consistency Check Not -
103437 Eth102/1/14 down* Not Consistency Check Not -
103438 Eth102/1/15 down* Not Consistency Check Not -
103439 Eth102/1/16 down* Not Consistency Check Not -
103440 Eth102/1/17 down* Not Consistency Check Not -
103441 Eth102/1/18 down* Not Consistency Check Not -
103442 Eth102/1/19 down* Not Consistency Check Not -
103443 Eth102/1/20 down* Not Consistency Check Not -
103444 Eth102/1/21 down* Not Consistency Check Not -
103445 Eth102/1/22 down* Not Consistency Check Not -
103446 Eth102/1/23 up success success 210
103447 Eth102/1/24 up success success 208
103448 Eth102/1/25 down* Not Consistency Check Not -
103449 Eth102/1/26 down* Not Consistency Check Not -
103450 Eth102/1/27 down* Not Consistency Check Not -
103451 Eth102/1/28 down* Not Consistency Check Not -
103452 Eth102/1/29 down* Not Consistency Check Not -
103453 Eth102/1/30 down* Not Consistency Check Not -
103454 Eth102/1/31 down* Not Consistency Check Not -
103455 Eth102/1/32 down* Not Consistency Check Not -
103456 Eth102/1/33 down* Not Consistency Check Not -
103457 Eth102/1/34 down* Not Consistency Check Not -
103458 Eth102/1/35 down* Not Consistency Check Not -
103459 Eth102/1/36 up success success 504
103460 Eth102/1/37 down* Not Consistency Check Not -
103461 Eth102/1/38 down* Not Consistency Check Not -
103462 Eth102/1/39 down* Not Consistency Check Not -
103463 Eth102/1/40 down* Not Consistency Check Not -
1034 Eth102/1/41 down* Not Consistency Check Not -
64 Applicable Performed
103465 Eth102/1/42 down* Not Consistency Check Not -
103468 Eth102/1/45 up success success 310
103469 Eth102/1/46 down* Not Consistency Check Not -
103470 Eth102/1/47 down* Not Consistency Check Not -
103471 Eth102/1/48 down* Not Consistency Check Not -
104448 Eth103/1/1 down* Not Consistency Check Not -
104449 Eth103/1/2 down* Not Consistency Check Not -
104450 Eth103/1/3 down* Not Consistency Check Not -
104451 Eth103/1/4 down* Not Consistency Check Not -
104452 Eth103/1/5 down* Not Consistency Check Not -
104453 Eth103/1/6 down* Not Consistency Check Not -
104454 Eth103/1/7 down* Not Consistency Check Not -
104455 Eth103/1/8 down* Not Consistency Check Not -
104456 Eth103/1/9 down* Not Consistency Check Not -
104457 Eth103/1/10 down* Not Consistency Check Not -
104458 Eth103/1/11 down* Not Consistency Check Not -
104459 Eth103/1/12 up success success 102
104460 Eth103/1/13 down* Not Consistency Check Not -
104461 Eth103/1/14 up success success 102
104462 Eth103/1/15 down* Not Consistency Check Not -
104463 Eth103/1/16 down* Not Consistency Check Not -
104464 Eth103/1/17 down* Not Consistency Check Not -
104465 Eth103/1/18 down* Not Consistency Check Not -
104466 Eth103/1/19 down* Not Consistency Check Not -
104467 Eth103/1/20 down* Not Consistency Check Not -
104468 Eth103/1/21 up success success 102
104469 Eth103/1/22 down* Not Consistency Check Not -
104470 Eth103/1/23 down* Not Consistency Check Not -
104471 Eth103/1/24 down* Not Consistency Check Not -
104472 Eth103/1/25 up success success 102
104473 Eth103/1/26 down* Not Consistency Check Not -
104474 Eth103/1/27 down* Not Consistency Check Not -
104475 Eth103/1/28 down* Not Consistency Check Not -
104476 Eth103/1/29 down* Not Consistency Check Not -
104477 Eth103/1/30 down* Not Consistency Check Not -
104478 Eth103/1/31 down* Not Consistency Check Not -
104479 Eth103/1/32 down* Not Consistency Check Not -
104480 Eth103/1/33 down* Not Consistency Check Not -
104481 Eth103/1/34 down* Not Consistency Check Not -
104482 Eth103/1/35 down* Not Consistency Check Not -
104483 Eth103/1/36 down* Not Consistency Check Not -
104484 Eth103/1/37 down* Not Consistency Check Not -
104485 Eth103/1/38 down* Not Consistency Check Not -
104486 Eth103/1/39 down* Not Consistency Check Not -
104487 Eth103/1/40 down* Not Consistency Check Not -
104488 Eth103/1/41 down* Not Consistency Check Not -
104489 Eth103/1/42 down* Not Consistency Check Not -
104490 Eth103/1/43 down* Not Consistency Check Not -
104491 Eth103/1/44 down* Not Consistency Check Not -
104492 Eth103/1/45 down* Not Consistency Check Not -
104493 Eth103/1/46 down* Not Consistency Check Not -
104494 Eth103/1/47 down* Not Consistency Check Not -
104495 Eth103/1/48 down* Not Consistency Check Not -
105472 Eth104/1/1 down* Not Consistency Check Not -
105473 Eth104/1/2 down* Not Consistency Check Not -
105474 Eth104/1/3 down* Not Consistency Check Not -
105475 Eth104/1/4 up success success 200
105476 Eth104/1/5 down* Not Consistency Check Not -
105477 Eth104/1/6 down* Not Consistency Check Not -
105478 Eth104/1/7 down* Not Consistency Check Not -
105479 Eth104/1/8 down* Not Consistency Check Not -
105480 Eth104/1/9 down* Not Consistency Check Not -
105481 Eth104/1/10 down* Not Consistency Check Not -
105482 Eth104/1/11 up success success 1
105483 Eth104/1/12 up success success 102
105484 Eth104/1/13 down* Not Consistency Check Not -
105485 Eth104/1/14 down* Not Consistency Check Not -
105486 Eth104/1/15 down* Not Consistency Check Not -
105487 Eth104/1/16 down* Not Consistency Check Not -
105488 Eth104/1/17 down* Not Consistency Check Not -
105489 Eth104/1/18 down* Not Consistency Check Not -
105490 Eth104/1/19 down* Not Consistency Check Not -
105491 Eth104/1/20 down* Not Consistency Check Not -
105492 Eth104/1/21 down* Not Consistency Check Not -
105493 Eth104/1/22 down* Not Consistency Check Not -
105494 Eth104/1/23 down* Not Consistency Check Not -
105495 Eth104/1/24 down* Not Consistency Check Not -
105496 Eth104/1/25 up success success 102
105497 Eth104/1/26 down* Not Consistency Check Not -
105498 Eth104/1/27 down* Not Consistency Check Not -
105499 Eth104/1/28 down* Not Consistency Check Not -
105500 Eth104/1/29 down* Not Consistency Check Not -
105501 Eth104/1/30 down* Not Consistency Check Not -
105502 Eth104/1/31 down* Not Consistency Check Not -
105503 Eth104/1/32 down* Not Consistency Check Not -
105504 Eth104/1/33 down* Not Consistency Check Not -
105505 Eth104/1/34 down* Not Consistency Check Not -
105506 Eth104/1/35 down* Not Consistency Check Not -
105507 Eth104/1/36 down* Not Consistency Check Not -
105508 Eth104/1/37 down* Not Consistency Check Not -
105509 Eth104/1/38 down* Not Consistency Check Not -
105510 Eth104/1/39 down* Not Consistency Check Not -
105511 Eth104/1/40 down* Not Consistency Check Not -
105512 Eth104/1/41 down* Not Consistency Check Not -
105513 Eth104/1/42 down* Not Consistency Check Not -
105514 Eth104/1/43 down* Not Consistency Check Not -
105515 Eth104/1/44 down* Not Consistency Check Not -
1055 Eth104/1/45 down* Not Consistency Check Not -
16 Applicable Performed
105517 Eth104/1/46 down* Not Consistency Check Not -
105518 Eth104/1/47 down* Not Consistency Check Not -
105519 Eth104/1/48 down* Not Consistency Check Not -
106500 Eth105/1/5 up success success 100,102
106501 Eth105/1/6 down* Not Consistency Check Not -
106502 Eth105/1/7 down* Not Consistency Check Not -
106503 Eth105/1/8 down* Not Consistency Check Not -
106504 Eth105/1/9 down* Not Consistency Check Not -
106505 Eth105/1/10 down* Not Consistency Check Not -
106506 Eth105/1/11 down* Not Consistency Check Not -
106507 Eth105/1/12 down* Not Consistency Check Not -
106508 Eth105/1/13 up success success 100,102
106509 Eth105/1/14 down* Not Consistency Check Not -
106510 Eth105/1/15 up success success 102
106511 Eth105/1/16 down* Not Consistency Check Not -
106512 Eth105/1/17 down* Not Consistency Check Not -
106513 Eth105/1/18 down* Not Consistency Check Not -
106514 Eth105/1/19 down* Not Consistency Check Not -
106515 Eth105/1/20 down* Not Consistency Check Not -
106516 Eth105/1/21 down* Not Consistency Check Not -
106517 Eth105/1/22 down* Not Consistency Check Not -
106518 Eth105/1/23 down* Not Consistency Check Not -
106519 Eth105/1/24 down* Not Consistency Check Not -
106520 Eth105/1/25 down* Not Consistency Check Not -
106521 Eth105/1/26 down* Not Consistency Check Not -
106522 Eth105/1/27 down* Not Consistency Check Not -
106523 Eth105/1/28 down* Not Consistency Check Not -
106524 Eth105/1/29 down* Not Consistency Check Not -
106525 Eth105/1/30 down* Not Consistency Check Not -
106526 Eth105/1/31 down* Not Consistency Check Not -
106527 Eth105/1/32 down* Not Consistency Check Not -
106528 Eth105/1/33 down* Not Consistency Check Not -
106529 Eth105/1/34 down* Not Consistency Check Not -
106530 Eth105/1/35 down* Not Consistency Check Not -
106531 Eth105/1/36 down* Not Consistency Check Not -
106532 Eth105/1/37 down* Not Consistency Check Not -
106533 Eth105/1/38 down* Not Consistency Check Not -
106534 Eth105/1/39 down* Not Consistency Check Not -
106535 Eth105/1/40 down* Not Consistency Check Not -
106536 Eth105/1/41 down* Not Consistency Check Not -
106537 Eth105/1/42 down* Not Consistency Check Not -
106538 Eth105/1/43 down* Not Consistency Check Not -
106539 Eth105/1/44 down* Not Consistency Check Not -
106540 Eth105/1/45 up success success 102
106541 Eth105/1/46 down* Not Consistency Check Not -
106542 Eth105/1/47 down* Not Consistency Check Not -
106543 Eth105/1/48 down* Not Consistency Check Not -
107524 Eth106/1/5 up success success 100,102
107525 Eth106/1/6 down* Not Consistency Check Not -
107526 Eth106/1/7 down* Not Consistency Check Not -
107527 Eth106/1/8 down* Not Consistency Check Not -
107528 Eth106/1/9 down* Not Consistency Check Not -
107529 Eth106/1/10 down* Not Consistency Check Not -
107530 Eth106/1/11 down* Not Consistency Check Not -
107531 Eth106/1/12 down* Not Consistency Check Not -
107532 Eth106/1/13 down* Not Consistency Check Not -
107533 Eth106/1/14 down* Not Consistency Check Not -
107534 Eth106/1/15 down* Not Consistency Check Not -
107535 Eth106/1/16 up success success 100,102
107536 Eth106/1/17 down* Not Consistency Check Not -
107537 Eth106/1/18 down* Not Consistency Check Not -
107538 Eth106/1/19 down* Not Consistency Check Not -
107539 Eth106/1/20 down* Not Consistency Check Not -
107540 Eth106/1/21 down* Not Consistency Check Not -
107541 Eth106/1/22 down* Not Consistency Check Not -
107542 Eth106/1/23 down* Not Consistency Check Not -
107543 Eth106/1/24 down* Not Consistency Check Not -
107544 Eth106/1/25 down* Not Consistency Check Not -
107545 Eth106/1/26 down* Not Consistency Check Not -
107546 Eth106/1/27 down* Not Consistency Check Not -
107547 Eth106/1/28 down* Not Consistency Check Not -
107548 Eth106/1/29 down* Not Consistency Check Not -
107549 Eth106/1/30 down* Not Consistency Check Not -
107550 Eth106/1/31 down* Not Consistency Check Not -
107551 Eth106/1/32 down* Not Consistency Check Not -
107552 Eth106/1/33 down* Not Consistency Check Not -
107553 Eth106/1/34 down* Not Consistency Check Not -
107554 Eth106/1/35 down* Not Consistency Check Not -
107555 Eth106/1/36 down* Not Consistency Check Not -
107556 Eth106/1/37 down* Not Consistency Check Not -
107557 Eth106/1/38 down* Not Consistency Check Not -
107558 Eth106/1/39 down* Not Consistency Check Not -
107559 Eth106/1/40 down* Not Consistency Check Not -
107560 Eth106/1/41 down* Not Consistency Check Not -
107561 Eth106/1/42 down* Not Consistency Check Not -
107562 Eth106/1/43 down* Not Consistency Check Not -
107563 Eth106/1/44 down* Not Consistency Check Not -
107564 Eth106/1/45 up success success 102
107565 Eth106/1/46 down* Not Consistency Check Not -
107566 Eth106/1/47 down* Not Consistency Check Not -
107567 Eth106/1/48 down* Not Consistency Check Not -
1085 Eth107/1/1 down* Not Consistency Check Not -
44 Applicable Performed
108545 Eth107/1/2 down* Not Consistency Check Not -
108546 Eth107/1/3 up success success 10
108547 Eth107/1/4 down* Not Consistency Check Not -
108548 Eth107/1/5 down* Not Consistency Check Not -
108549 Eth107/1/6 up success success 202
108550 Eth107/1/7 up success success 202
108551 Eth107/1/8 up success success 100
108552 Eth107/1/9 up success success 202
108553 Eth107/1/10 down* Not Consistency Check Not -
108554 Eth107/1/11 down* Not Consistency Check Not -
108555 Eth107/1/12 up success success 102
108556 Eth107/1/13 up success success 100
108557 Eth107/1/14 up success success 210
108558 Eth107/1/15 up success success 200-203,212
,501-503
108559 Eth107/1/16 up success success 102
108560 Eth107/1/17 down* Not Consistency Check Not -
108561 Eth107/1/18 down* Not Consistency Check Not -
108562 Eth107/1/19 down* Not Consistency Check Not -
108563 Eth107/1/20 down* Not Consistency Check Not -
108564 Eth107/1/21 down* Not Consistency Check Not -
108565 Eth107/1/22 down* Not Consistency Check Not -
108566 Eth107/1/23 up success success 200
108567 Eth107/1/24 up success success 100
108568 Eth107/1/25 up success success 210
108569 Eth107/1/26 up success success 200-201,212
,501
108570 Eth107/1/27 up success success 100
108571 Eth107/1/28 down* Not Consistency Check Not -
108572 Eth107/1/29 down* Not Consistency Check Not -
108573 Eth107/1/30 down* Not Consistency Check Not -
108574 Eth107/1/31 down* Not Consistency Check Not -
108575 Eth107/1/32 down* Not Consistency Check Not -
108576 Eth107/1/33 down* Not Consistency Check Not -
108577 Eth107/1/34 down* Not Consistency Check Not -
108578 Eth107/1/35 down* Not Consistency Check Not -
108579 Eth107/1/36 down* Not Consistency Check Not -
108580 Eth107/1/37 down* Not Consistency Check Not -
108581 Eth107/1/38 down* Not Consistency Check Not -
108582 Eth107/1/39 down* Not Consistency Check Not -
108583 Eth107/1/40 down* Not Consistency Check Not -
108584 Eth107/1/41 down* Not Consistency Check Not -
108585 Eth107/1/42 down* Not Consistency Check Not -
108586 Eth107/1/43 down* Not Consistency Check Not -
108587 Eth107/1/44 down* Not Consistency Check Not -
108588 Eth107/1/45 up success success 102
108589 Eth107/1/46 down* Not Consistency Check Not -
108590 Eth107/1/47 down* Not Consistency Check Not -
108591 Eth107/1/48 down* Not Consistency Check Not -
109568 Eth108/1/1 down* Not Consistency Check Not -
109569 Eth108/1/2 down* Not Consistency Check Not -
109570 Eth108/1/3 up success success 10
109571 Eth108/1/4 up success success 100
109572 Eth108/1/5 down* Not Consistency Check Not -
109573 Eth108/1/6 up success success 202
109574 Eth108/1/7 up success success 202
109575 Eth108/1/8 up success success 102
109576 Eth108/1/9 up success success 202
109577 Eth108/1/10 down* Not Consistency Check Not -
109578 Eth108/1/11 down* Not Consistency Check Not -
109579 Eth108/1/12 down* Not Consistency Check Not -
109580 Eth108/1/13 down* Not Consistency Check Not -
109581 Eth108/1/14 up success success 210
109582 Eth108/1/15 up success success 200-203,212
,501-503
109583 Eth108/1/16 down* Not Consistency Check Not -
109584 Eth108/1/17 down* Not Consistency Check Not -
109585 Eth108/1/18 down* Not Consistency Check Not -
109586 Eth108/1/19 down* Not Consistency Check Not -
109587 Eth108/1/20 down* Not Consistency Check Not -
109588 Eth108/1/21 down* Not Consistency Check Not -
109589 Eth108/1/22 down* Not Consistency Check Not -
109590 Eth108/1/23 up success success 200
109591 Eth108/1/24 up success success 102
109592 Eth108/1/25 up success success 210
109593 Eth108/1/26 up success success 200-201,212
,501
109594 Eth108/1/27 down* Not Consistency Check Not -
109595 Eth108/1/28 down* Not Consistency Check Not -
109596 Eth108/1/29 down* Not Consistency Check Not -
109597 Eth108/1/30 down* Not Consistency Check Not -
109598 Eth108/1/31 down* Not Consistency Check Not -
109599 Eth108/1/32 down* Not Consistency Check Not -
109600 Eth108/1/33 down* Not Consistency Check Not -
109601 Eth108/1/34 down* Not Consistency Check Not -
109602 Eth108/1/35 down* Not Consistency Check Not -
109603 Eth108/1/36 down* Not Consistency Check Not -
109604 Eth108/1/37 down* Not Consistency Check Not -
109605 Eth108/1/38 down* Not Consistency Check Not -
109606 Eth108/1/39 down* Not Consistency Check Not -
109607 Eth108/1/40 down* Not Consistency Check Not -
109608 Eth108/1/41 down* Not Consistency Check Not -
109609 Eth108/1/42 down* Not Consistency Check Not -
109610 Eth108/1/43 down* Not Consistency Check Not -
109611 Eth108/1/44 down* Not Consistency Check Not -
109612 Eth108/1/45 down* Not Consistency Check Not -
109613 Eth108/1/46 down* Not Consistency Check Not -
109614 Eth108/1/47 down* Not Consistency Check Not -
109615 Eth108/1/48 down* Not Consistency Check Not -
110592 Eth109/1/1 up success success 203
110593 Eth109/1/2 down* Not Consistency Check Not -
110594 Eth109/1/3 down* Not Consistency Check Not -
110595 Eth109/1/4 down* Not Consistency Check Not -
1105 Eth109/1/5 down* Not Consistency Check Not -
96 Applicable Performed
110597 Eth109/1/6 down* Not Consistency Check Not -
110598 Eth109/1/7 up success success 102
110599 Eth109/1/8 up success success 102
110600 Eth109/1/9 down* Not Consistency Check Not -
110601 Eth109/1/10 down* Not Consistency Check Not -
110602 Eth109/1/11 up success success 102
110603 Eth109/1/12 down* Not Consistency Check Not -
110604 Eth109/1/13 down* Not Consistency Check Not -
110605 Eth109/1/14 down* Not Consistency Check Not -
110606 Eth109/1/15 down* Not Consistency Check Not -
110607 Eth109/1/16 down* Not Consistency Check Not -
110608 Eth109/1/17 down* Not Consistency Check Not -
110609 Eth109/1/18 up success success 102
110610 Eth109/1/19 down* Not Consistency Check Not -
110611 Eth109/1/20 up success success 102
110612 Eth109/1/21 down* Not Consistency Check Not -
110613 Eth109/1/22 down* Not Consistency Check Not -
110614 Eth109/1/23 down* Not Consistency Check Not -
110615 Eth109/1/24 down* Not Consistency Check Not -
110616 Eth109/1/25 up success success 203
110617 Eth109/1/26 down* Not Consistency Check Not -
110618 Eth109/1/27 down* Not Consistency Check Not -
110619 Eth109/1/28 down* Not Consistency Check Not -
110620 Eth109/1/29 down* Not Consistency Check Not -
110621 Eth109/1/30 up success success 102
110622 Eth109/1/31 up success success 102
110623 Eth109/1/32 up success success 102
110624 Eth109/1/33 down* Not Consistency Check Not -
110625 Eth109/1/34 down* Not Consistency Check Not -
110626 Eth109/1/35 up success success 102
110627 Eth109/1/36 up success success 102
110628 Eth109/1/37 down* Not Consistency Check Not -
110629 Eth109/1/38 down* Not Consistency Check Not -
110630 Eth109/1/39 down* Not Consistency Check Not -
110631 Eth109/1/40 down* Not Consistency Check Not -
110632 Eth109/1/41 down* Not Consistency Check Not -
110633 Eth109/1/42 down* Not Consistency Check Not -
110634 Eth109/1/43 down* Not Consistency Check Not -
110635 Eth109/1/44 down* Not Consistency Check Not -
110636 Eth109/1/45 up success success 102
110637 Eth109/1/46 up success success 102
110638 Eth109/1/47 down* Not Consistency Check Not -
110639 Eth109/1/48 up success success 102
111616 Eth110/1/1 down* Not Consistency Check Not -
111617 Eth110/1/2 down* Not Consistency Check Not -
111618 Eth110/1/3 down* Not Consistency Check Not -
111619 Eth110/1/4 down* Not Consistency Check Not -
111620 Eth110/1/5 down* Not Consistency Check Not -
111621 Eth110/1/6 down* Not Consistency Check Not -
111622 Eth110/1/7 down* Not Consistency Check Not -
111623 Eth110/1/8 down* Not Consistency Check Not -
111624 Eth110/1/9 down* Not Consistency Check Not -
111625 Eth110/1/10 down* Not Consistency Check Not -
111626 Eth110/1/11 down* Not Consistency Check Not -
111627 Eth110/1/12 down* Not Consistency Check Not -
111628 Eth110/1/13 down* Not Consistency Check Not -
111629 Eth110/1/14 down* Not Consistency Check Not -
111630 Eth110/1/15 down* Not Consistency Check Not -
111631 Eth110/1/16 down* Not Consistency Check Not -
111632 Eth110/1/17 down* Not Consistency Check Not -
111633 Eth110/1/18 down* Not Consistency Check Not -
111634 Eth110/1/19 down* Not Consistency Check Not -
111635 Eth110/1/20 down* Not Consistency Check Not -
111636 Eth110/1/21 down* Not Consistency Check Not -
111637 Eth110/1/22 down* Not Consistency Check Not -
111638 Eth110/1/23 down* Not Consistency Check Not -
111639 Eth110/1/24 down* Not Consistency Check Not -
111640 Eth110/1/25 down* Not Consistency Check Not -
111641 Eth110/1/26 down* Not Consistency Check Not -
111642 Eth110/1/27 down* Not Consistency Check Not -
111643 Eth110/1/28 down* Not Consistency Check Not -
111644 Eth110/1/29 down* Not Consistency Check Not -
111645 Eth110/1/30 down* Not Consistency Check Not -
111646 Eth110/1/31 down* Not Consistency Check Not -
111647 Eth110/1/32 down* Not Consistency Check Not -
111648 Eth110/1/33 down* Not Consistency Check Not -
111649 Eth110/1/34 down* Not Consistency Check Not -
111650 Eth110/1/35 down* Not Consistency Check Not -
111651 Eth110/1/36 down* Not Consistency Check Not -
111652 Eth110/1/37 down* Not Consistency Check Not -
111653 Eth110/1/38 down* Not Consistency Check Not -
111654 Eth110/1/39 down* Not Consistency Check Not -
111655 Eth110/1/40 down* Not Consistency Check Not -
111656 Eth110/1/41 down* Not Consistency Check Not -
111657 Eth110/1/42 down* Not Consistency Check Not -
111658 Eth110/1/43 down* Not Consistency Check Not -
111659 Eth110/1/44 down* Not Consistency Check Not -
111660 Eth110/1/45 down* Not Consistency Check Not -
111661 Eth110/1/46 down* Not Consistency Check Not -
111662 Eth110/1/47 down* Not Consistency Check Not -
111663 Eth110/1/48 down* Not Consistency Check Not -
112640 Eth111/1/1 down* Not Consistency Check Not -
112641 Eth111/1/2 up success success 208
112642 Eth111/1/3 up success success 711
112643 Eth111/1/4 down* Not Consistency Check Not -
112644 Eth111/1/5 down* Not Consistency Check Not -
112645 Eth111/1/6 up success success 700-702,710
-711,730-73
1,800
112646 Eth111/1/7 down* Not Consistency Check Not -
112647 Eth111/1/8 down* Not Consistency Check Not -
1126 Eth111/1/9 up success success 102
48
112649 Eth111/1/10 down* Not Consistency Check Not -
112650 Eth111/1/11 up success success 690
112651 Eth111/1/12 down* Not Consistency Check Not -
112652 Eth111/1/13 down* Not Consistency Check Not -
112653 Eth111/1/14 down* Not Consistency Check Not -
112654 Eth111/1/15 down* Not Consistency Check Not -
112655 Eth111/1/16 down* Not Consistency Check Not -
112656 Eth111/1/17 down* Not Consistency Check Not -
112657 Eth111/1/18 down* Not Consistency Check Not -
112658 Eth111/1/19 down* Not Consistency Check Not -
112659 Eth111/1/20 down* Not Consistency Check Not -
112660 Eth111/1/21 down* Not Consistency Check Not -
112661 Eth111/1/22 up success success 102
112662 Eth111/1/23 up success success 210
112663 Eth111/1/24 up success success 208
112664 Eth111/1/25 up success success 100
112665 Eth111/1/26 up success success 210
112666 Eth111/1/27 up success success 208
112667 Eth111/1/28 up success success 208
112668 Eth111/1/29 up success success 999
112669 Eth111/1/30 up success success 711
112670 Eth111/1/31 up success success 700
112671 Eth111/1/32 down* Not Consistency Check Not -
112672 Eth111/1/33 down* Not Consistency Check Not -
112673 Eth111/1/34 down* Not Consistency Check Not -
112674 Eth111/1/35 down* Not Consistency Check Not -
112675 Eth111/1/36 up success success 504
112676 Eth111/1/37 down* Not Consistency Check Not -
112677 Eth111/1/38 down* Not Consistency Check Not -
112678 Eth111/1/39 down* Not Consistency Check Not -
112679 Eth111/1/40 down* Not Consistency Check Not -
112681 Eth111/1/42 up success success 102
112684 Eth111/1/45 down* Not Consistency Check Not -
112685 Eth111/1/46 down* Not Consistency Check Not -
112686 Eth111/1/47 down* Not Consistency Check Not -
112687 Eth111/1/48 down* Not Consistency Check Not -
113664 Eth112/1/1 down* Not Consistency Check Not -
113665 Eth112/1/2 down* Not Consistency Check Not -
113666 Eth112/1/3 up success success 711
113667 Eth112/1/4 down* Not Consistency Check Not -
113668 Eth112/1/5 down* Not Consistency Check Not -
113669 Eth112/1/6 up success success 700-702,710
-711,730-73
1,800
113670 Eth112/1/7 up success success 711
113671 Eth112/1/8 down* Not Consistency Check Not -
113672 Eth112/1/9 up success success 800
113673 Eth112/1/10 down* Not Consistency Check Not -
113674 Eth112/1/11 down* Not Consistency Check Not -
113675 Eth112/1/12 up success success 690
113676 Eth112/1/13 up success success 690
113677 Eth112/1/14 down* Not Consistency Check Not -
113678 Eth112/1/15 down* Not Consistency Check Not -
113679 Eth112/1/16 down* Not Consistency Check Not -
113680 Eth112/1/17 up success success 100
113681 Eth112/1/18 down* Not Consistency Check Not -
113682 Eth112/1/19 up success success 1
113683 Eth112/1/20 down* Not Consistency Check Not -
113684 Eth112/1/21 up success success 102
113685 Eth112/1/22 down* Not Consistency Check Not -
113686 Eth112/1/23 up success success 210
113687 Eth112/1/24 up success success 208
113688 Eth112/1/25 up success success 100
113689 Eth112/1/26 up success success 210
113690 Eth112/1/27 up success success 208
113691 Eth112/1/28 up success success 208
113692 Eth112/1/29 up success success 999
113693 Eth112/1/30 down* Not Consistency Check Not -
113694 Eth112/1/31 down* Not Consistency Check Not -
113695 Eth112/1/32 down* Not Consistency Check Not -
113696 Eth112/1/33 down* Not Consistency Check Not -
113697 Eth112/1/34 down* Not Consistency Check Not -
113698 Eth112/1/35 down* Not Consistency Check Not -
113699 Eth112/1/36 up success success 504
113700 Eth112/1/37 down* Not Consistency Check Not -
113701 Eth112/1/38 down* Not Consistency Check Not -
113702 Eth112/1/39 down* Not Consistency Check Not -
113703 Eth112/1/40 down* Not Consistency Check Not -
113704 Eth112/1/41 down* Not Consistency Check Not -
113705 Eth112/1/42 down* Not Consistency Check Not -
113706 Eth112/1/43 down* Not Consistency Check Not -
113707 Eth112/1/44 down* Not Consistency Check Not -
113708 Eth112/1/45 down* Not Consistency Check Not -
113709 Eth112/1/46 down* Not Consistency Check Not -
113710 Eth112/1/47 up success success 102
113711 Eth112/1/48 up success success 102
262153 Po10 up success success 10,102-104,
200-204,206
-208,210-21
2,214,310,5
01-503,1100
262154 Po11 up success success 10,102-104,
200-204,206
-208,210-21
2,214,310,5
01-503,1100
262163 Po20 up success success 103
262164 Po21 up success success 103
