5108 chassis and power failure
MrTan
Hello all,
I have a fully populated 5108 chassis with 8 x B200 M5 servers.
The chassis has 4 power supplies which are configured in a grid mode.
Power supply 1+2 are connected to the same PDU and power supply 3+4
are connected to a different PDU.
What will happen if I lose one of the PDU's, will the chassis be able to handle
all the 8 x B200 M5 servers at full power?
Thanks in advance,
Ron.
balaji.bandi
if you configured Grid Mode : ( as per my experience you are ok, if one of the PDU) - Hope you have 2 Different source of Power - Essential and non essential kind.
My Live environment running, when i do sat test before put them in to production it was ok, as of now, not seen any Power failures.
Grid – Two power sources are turned on, or the chassis requires greater than N+1 redundancy. If one source fails (which causes a loss of power to one or two power supplies), the surviving power supplies on the other power circuit continue to provide power to the chassis.
BB
Each PSU is capable of handling 2500W. 4 x 2500W = 10000W.
If 2 PSU's will fail (that means that one PDU is down), the chassis
will have half of its power which means 5000W.
I have calculated the amount of power required for the 8 x B200
servers on the Cisco UCS Power Calculator website
(https://ucspowercalc.cloudapps.cisco.com/public/index.jsp)
and got a result of 5250W.
5250W is more than 5000W. What will happen to the servers?
You could check your current power usage via UCS Manager:
Select Chassis -> Power -> Statistics
There you can see the average, max and min usage summarized for the chassis and also separated for the servers.
I checked some of our chassis, e.g. a fully populated 5108-AC2 with 8 running B200 M5 servers consumes max 2464W.
I can remeber we did several outage tests some time ago and the chassis could handle the failure of 2 psus.