09-06-2024 11:58 AM
Hello,
We noticed we have an issue with faulty fans on a Cisco Integrated Management Controller. After reviewing the logs, I need some clarification on what fans are failing.
2024-09-06T11:01:20 | Critical | F0397 | sys/rack-unit-1/fan-module-1-5/fan-2 | performance-problem | MOD5_FAN2_SPEED: Fan speed for fan-10 is lower non recoverable : Check the air intake to the server |
2024-09-06T11:01:20 | Critical | F0397 | sys/rack-unit-1/fan-module-1-3/fan-2 | performance-problem | MOD3_FAN2_SPEED: Fan speed for fan-6 is lower non recoverable : Check the air intake to the server |
We replaced fans 2 and 6 per this notification we received via email from the controller
Server HostName:C220-WZP23300NTG
Severity: critical
Fault Code: F0397
Problem Cause: performance-problem
Entity DN: sys/rack-unit-1/fan-module-1-3/fan-2
Description: MOD3_FAN2_SPEED: Fan speed for fan-6 is lower non recoverable : Check the air intake to the server
PLATFORM:
CIMC Ver: 4.0(4b)
BIOS Ver: C220M5.4.0.4b.0.0407190256
I need some clarification on how to read this. From the data in the table I shared are the fans 5 and 3 need to be replaced or 10 and 6?
Thank you
09-08-2024 11:56 PM
Ref : https://www.cisco.com/c/en/us/td/docs/unified_computing/ucs/c/sw/fault/reference/guide/Cisco_UCS_C-Series_Servers_CIMC_Faults/CIMC_Faults.html
>....
Start reading from : fltEquipmentFanPerfThresholdNonRecoverable
M.
09-09-2024 01:22 AM
From the serial number you provided, it’s a UCS 220 M5 with 7 fans. According to the OP, there are issues with Modules 3 and 5. Please replace Fans 3 and 5 and check if that resolves the problem
09-09-2024 06:51 AM
UCS C-Series fan error messages are obtuse at best.
Each fan module has two spinning fans.
So divide the Alarm Description "fan-#" by two or only pay attention to the "MOD#".
Human comprehension | Alarm DNs | Alarm Description |
Fan 1 |
sys/rack-unit-1/fan-module-1-1/fan-1 |
MOD1_FAN1_SPEED: Fan speed for fan-1 |
Fan 2 | sys/rack-unit-1/fan-module-1-2/fan-1 sys/rack-unit-1/fan-module-1-2/fan-2 |
MOD2_FAN1_SPEED: Fan speed for fan-3 |
Fan 3 | sys/rack-unit-1/fan-module-1-3/fan-1 sys/rack-unit-1/fan-module-1-3/fan-2 |
MOD3_FAN1_SPEED: Fan speed for fan-5 |
Fan 4 | sys/rack-unit-1/fan-module-1-4/fan-1 sys/rack-unit-1/fan-module-1-4/fan-2 |
MOD4_FAN1_SPEED: Fan speed for fan-7 |
Fan 5 | sys/rack-unit-1/fan-module-1-5/fan-1 sys/rack-unit-1/fan-module-1-5/fan-2 |
MOD5_FAN1_SPEED: Fan speed for fan-9 |
Fan 6 | sys/rack-unit-1/fan-module-1-6/fan-1 sys/rack-unit-1/fan-module-1-6/fan-2 |
MOD6_FAN1_SPEED: Fan speed for fan-11 |
Fan 7 | sys/rack-unit-1/fan-module-1-7/fan-1 sys/rack-unit-1/fan-module-1-7/fan-2 |
MOD7_FAN1_SPEED: Fan speed for fan-13 |