Difference between PWR-4.4KW-DC-V3 and PWR-2KW-DC-V2

anandbhalla
Level 1
Level 1

Hi,

We intend to deploy ASR-9010-SYS using DC power.

Day 1 hardware configuration typically consists of 2xRSP-880-SE, 2xMOD-160, FAN-V2. This configuration will grow in coming months and we may add 4x100G / 8x100G line cards to this router system.

We have option of either using PWR-2KW-DC-V2 or PWR-4.4KW-DC-V3

I understand that having the above configuration, we will need either 3xPWR-2KW-DC-V2 or 2xPWR-4.4KW-DC-V3 for n+1 power redundancy.

Wanted to understand how these two DC power modules are different. 

We have experience on 2.1KW, but none for 4.4KW

If my understanding is correct: 2.1KW had 2 input feeds, and they work in active / standby mode. Hence only 2KW power drawn per module.

Is it that with the 4.4KW module both the input feeds are working in active/active mode? Hence drawing complete 4.4KW of power per module.

If there is a document detailing the mechanism, please point me there.

Thanks :)

Br //Anand

6 Replies 6

Sameer Avadhani
Cisco Employee
Cisco Employee

Hello Anand, 

The difference is that for V3, we have two inputs which contribute 2.2kW each to get the 4.4kW output.

Your understanding seems correct. 

Hello Sameer:

Can we use both Power Modules in the same ASR9010 Chassis?

Thanks

Hi,

I highly doubt that this is possible because the Power Entry modules are different.

You have A9K-AC-PEM-V3 and A9K-AC-PEM-V2.

In case of PEMv1 and PEMv2 it was necessary to change the EEPROM values for v2.

If possible go with v3 because of future upgrades on the chassis.

Hello,

And if I use PEM-V2 for 2.2kW and PEM-V3 for 4.4kW in the same chassis. Is it an option? Will work?

I want to use this scenario only by a while in a migration process in ASR9100 to replace PEM-V2 for PEM-V3 without shutdown all chassis.

I want to replace those as follow:

Actual: Power Tray 1 – PEM-V2 – with 2xPWR-2KW-DC-V2
Power Tray 0 – PEM-V2 – with 2xPWR-2KW-DC-V2


Step 1: Shutdown Power Tray 1 to replace with PEM-V3/PM and power-on. Both PEM and Power Modules can be active at the same time??
Power Tray 1 – PEM-V3 – with 1xPWR-4.4KW-DC-V3
Power Tray 0 – PEM-V2 – with 2xPWR-2KW-DC-V2

Step 2: Shutdown Power Tray 0 to replace with PEM-V3/PM and power-on.
Power Tray 1 – PEM-V3 – with 1xPWR-4.4KW-DC-V3
Power Tray 0 – PEM-V3 – with 1xPWR-4.4KW-DC-V3

Thank you for your answers and comments!!

You got me here. My knowledge about this part is limited. 

I hope that someone from Cisco can help you out.

My recommendation is to have a maintenance window so you can shut down the chassis and replace the PEMs and PS.

Different PEM types in the same chassis are not supported. Migrating from PEM-v2 to PEM-v3 requires a power down of the chassis.