02-17-2013 03:22 PM - edited 03-16-2019 03:46 PM
This command is showing me the following alarms in two E1 interfaces. What troubleshooting should I do? I see alarms in: slip secs, Fr Loss Secs, Line Err Secs, Degraded mins, etc, etc.
Shoul I also check something in the CUCM (ver. 8.6.2.20000-2)?
E1 0/1/0 is up.
Applique type is Channelized E1 - balanced
No alarms detected.
alarm-trigger is not set
Version info FPGA Rev: 08121917, FPGA Type: PRK4
Framing is NO-CRC4, Line Code is HDB3, Clock Source is Line.
International Bit: 1, National Bits: 11111
Data in current interval (579 seconds elapsed):
0 Line Code Violations, 0 Path Code Violations
0 Slip Secs, 0 Fr Loss Secs, 0 Line Err Secs, 0 Degraded Mins
0 Errored Secs, 0 Bursty Err Secs, 0 Severely Err Secs, 0 Unavail Secs
Total Data (last 24 hours)
446 Line Code Violations, 522 Path Code Violations,
2 Slip Secs, 48 Fr Loss Secs, 2 Line Err Secs, 3 Degraded Mins,
134 Errored Secs, 26 Bursty Err Secs, 0 Severely Err Secs, 50 Unavail Secs
E1 0/1/1 is up.
Applique type is Channelized E1 - balanced
No alarms detected.
alarm-trigger is not set
Version info FPGA Rev: 08121917, FPGA Type: PRK4
Framing is NO-CRC4, Line Code is HDB3, Clock Source is Line.
International Bit: 1, National Bits: 11111
Data in current interval (579 seconds elapsed):
0 Line Code Violations, 0 Path Code Violations
200 Slip Secs, 0 Fr Loss Secs, 0 Line Err Secs, 0 Degraded Mins
200 Errored Secs, 0 Bursty Err Secs, 0 Severely Err Secs, 0 Unavail Secs
Total Data (last 24 hours)
0 Line Code Violations, 0 Path Code Violations,
29774 Slip Secs, 0 Fr Loss Secs, 0 Line Err Secs, 0 Degraded Mins,
29774 Errored Secs, 0 Bursty Err Secs, 0 Severely Err Secs, 0 Unavail Secs
Thanks for any help.
Best,
Patricio
Solved! Go to Solution.
- Labels:
-
Other IP Telephony
Accepted Solutions

- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
02-17-2013 03:40 PM
Those errors are layer 1 errors with the E1 circuit if they are still incrementing. Clear the counters, show controller a few times and if the errors are increasing then check the cable between router interface and smartjack.
Call your provider and have them
Test the circuit for issues.
Sent from Cisco Technical Support iPhone App
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
02-17-2013 03:53 PM
Hi Patricio,
This errors appear generally when you have a cable problem, try to replace the E1 cable....
Regards
Please rate all useful posts
Favor calificar todos las respuestas útiles.
_____________________________
LinkedIn Profile: do.linkedin.com/in/leosalcie
MDGDP, CCNA, CCNA Voice certified
Please remember to rate useful posts clicking on the stars below.
LinkedIn Profile: do.linkedin.com/in/leosalcie

- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
02-17-2013 03:40 PM
Those errors are layer 1 errors with the E1 circuit if they are still incrementing. Clear the counters, show controller a few times and if the errors are increasing then check the cable between router interface and smartjack.
Call your provider and have them
Test the circuit for issues.
Sent from Cisco Technical Support iPhone App
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
02-17-2013 03:47 PM
Ok, thank you for your response.
If there's any other suggestions, they are very welcomed.
Patricio
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
02-17-2013 03:53 PM
Hi Patricio,
This errors appear generally when you have a cable problem, try to replace the E1 cable....
Regards
Please rate all useful posts
Favor calificar todos las respuestas útiles.
_____________________________
LinkedIn Profile: do.linkedin.com/in/leosalcie
MDGDP, CCNA, CCNA Voice certified
Please remember to rate useful posts clicking on the stars below.
LinkedIn Profile: do.linkedin.com/in/leosalcie
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
02-17-2013 05:24 PM
Thank you Leo.
Replacing the cable will absolutely resolve the problem?
After 515 minutes, it's showing this info now:
E1 0/1/0 is up.
Applique type is Channelized E1 - balanced
No alarms detected.
alarm-trigger is not set
Version info FPGA Rev: 08121917, FPGA Type: PRK4
Framing is NO-CRC4, Line Code is HDB3, Clock Source is Line.
International Bit: 1, National Bits: 11111
Data in current interval (99 seconds elapsed):
0 Line Code Violations, 0 Path Code Violations
0 Slip Secs, 0 Fr Loss Secs, 0 Line Err Secs, 0 Degraded Mins
0 Errored Secs, 0 Bursty Err Secs, 0 Severely Err Secs, 0 Unavail Secs
Total Data (last 5 15 minute intervals):
0 Line Code Violations, 0 Path Code Violations,
0 Slip Secs, 0 Fr Loss Secs, 0 Line Err Secs, 0 Degraded Mins,
0 Errored Secs, 0 Bursty Err Secs, 0 Severely Err Secs, 0 Unavail Secs
E1 0/1/1 is up.
Applique type is Channelized E1 - balanced
Description: ## TRAMA CLARO 5551-0600 ##
No alarms detected.
alarm-trigger is not set
Version info FPGA Rev: 08121917, FPGA Type: PRK4
Framing is NO-CRC4, Line Code is HDB3, Clock Source is Line.
International Bit: 1, National Bits: 11111
Data in current interval (99 seconds elapsed):
0 Line Code Violations, 0 Path Code Violations
35 Slip Secs, 0 Fr Loss Secs, 0 Line Err Secs, 0 Degraded Mins
35 Errored Secs, 0 Bursty Err Secs, 0 Severely Err Secs, 0 Unavail Secs
Total Data (last 5 15 minute intervals):
0 Line Code Violations, 0 Path Code Violations,
1550 Slip Secs, 0 Fr Loss Secs, 0 Line Err Secs, 0 Degraded Mins,
1550 Errored Secs, 0 Bursty Err Secs, 0 Severely Err Secs, 0 Unavail Secs
Patricio
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
02-17-2013 05:39 PM
And now:
E1 0/1/0 is up.
Applique type is Channelized E1 - balanced
No alarms detected.
alarm-trigger is not set
Version info FPGA Rev: 08121917, FPGA Type: PRK4
Framing is NO-CRC4, Line Code is HDB3, Clock Source is Line.
International Bit: 1, National Bits: 11111
Data in current interval (374 seconds elapsed):
0 Line Code Violations, 0 Path Code Violations
0 Slip Secs, 0 Fr Loss Secs, 0 Line Err Secs, 0 Degraded Mins
0 Errored Secs, 0 Bursty Err Secs, 0 Severely Err Secs, 0 Unavail Secs
Total Data (last 6 15 minute intervals):
211 Line Code Violations, 268 Path Code Violations,
1 Slip Secs, 23 Fr Loss Secs, 2 Line Err Secs, 1 Degraded Mins,
102 Errored Secs, 16 Bursty Err Secs, 0 Severely Err Secs, 20 Unavail Secs
E1 0/1/1 is up.
Applique type is Channelized E1 - balanced
Description: ## TRAMA CLARO 5551-0600 ##
No alarms detected.
alarm-trigger is not set
Version info FPGA Rev: 08121917, FPGA Type: PRK4
Framing is NO-CRC4, Line Code is HDB3, Clock Source is Line.
International Bit: 1, National Bits: 11111
Data in current interval (374 seconds elapsed):
0 Line Code Violations, 0 Path Code Violations
128 Slip Secs, 0 Fr Loss Secs, 0 Line Err Secs, 0 Degraded Mins
128 Errored Secs, 0 Bursty Err Secs, 0 Severely Err Secs, 0 Unavail Secs
Total Data (last 6 15 minute intervals):
0 Line Code Violations, 0 Path Code Violations,
1861 Slip Secs, 0 Fr Loss Secs, 0 Line Err Secs, 0 Degraded Mins,
1861 Errored Secs, 0 Bursty Err Secs, 0 Severely Err Secs, 0 Unavail Secs