03-27-2019 10:23 PM
Good Day to All,
I am trying to calculate the " Environment factors like power and cooling variable for Nexus 9500 switches ( mainly 9516 and 9504) to calculate the facility requirements.
Electrical
Volts= Available in data sheets
Ø = Not available
Wires = Not clear
Amp= Available in data sheets
Cooling
KBTU/Hr = Available in data sheets
KW = Available in power tool
Tons= Not available in data sheets
CFM = Not Available in data sheets
Does any body have any idea how to find them.
Thanks
Solved! Go to Solution.
03-28-2019 08:59 AM
Hello
In the data center, heat is often removed from the equipment by increasing the airflow, this is expressed in CFM, an increase in CFM equates to an increase in heat removal. There must be enough CFM that the equipment does not overheat. so the larger fan modules you have on the chassis the better cooling you will get for the chassis and its modules.
In other hand, talking about tons, remember that air contiditoning systems are rated in tons, so this refers to your data center cooling system, this is not actually the same if we talk about a Nexus chassis, you know that the role played by a fan module in the chassis is to take the cold aisle air flow, cool the internal components, thereby releasing the hot air from the chassis.
I am not an especialist in data center design, nevertheless I think you're trying to find information that is not concerned to the Cisco equipment, but to your data center cooling system desing. So this documentation could be useful for you.
https://www.cedengineering.com/userfiles/HVAC%20Cooling%20Systems%20for%20Data%20Centers.pdf
HTH
03-28-2019 12:54 AM
Hi,
I am not sure about cooling information but you can find power details here:
Regards,
Deepak Kumar
03-28-2019 01:41 AM
03-28-2019 03:16 AM
Look here for the Nexus 95XX
03-28-2019 05:56 AM
03-28-2019 08:59 AM
Hello
In the data center, heat is often removed from the equipment by increasing the airflow, this is expressed in CFM, an increase in CFM equates to an increase in heat removal. There must be enough CFM that the equipment does not overheat. so the larger fan modules you have on the chassis the better cooling you will get for the chassis and its modules.
In other hand, talking about tons, remember that air contiditoning systems are rated in tons, so this refers to your data center cooling system, this is not actually the same if we talk about a Nexus chassis, you know that the role played by a fan module in the chassis is to take the cold aisle air flow, cool the internal components, thereby releasing the hot air from the chassis.
I am not an especialist in data center design, nevertheless I think you're trying to find information that is not concerned to the Cisco equipment, but to your data center cooling system desing. So this documentation could be useful for you.
https://www.cedengineering.com/userfiles/HVAC%20Cooling%20Systems%20for%20Data%20Centers.pdf
HTH