Power supply # in chassis # power: off

robinsonjas
Level 1
Level 1

Have 4 new UCS chassis in rack. 3 of them have PSUs 2 & 4 in an 'off' state, even though the green light is lit on all 4 PSUs in the chassis. All chassis are plugged in same PDU in rear of rack so I know we have clean power.

I have tried setting from Grid to N+1 and back to no avail. Any tips would be helpful

Chassis 1:
    Overall Status: Power Problem
    Operability: Operable
    Power State: Ok
    Thermal Status: Ok

    PSU 1:
        Threshold Status: OK
        Overall Status: Operable
        Operability: Operable
        Power State: On
        Thermal Status: OK
        Voltage Status: OK

    PSU 2:
        Threshold Status: N/A
        Overall Status: N/A
        Operability: N/A
        Power State: Off
        Thermal Status: N/A
        Voltage Status: N/A

    PSU 3:
        Threshold Status: N/A
        Overall Status: Operable
        Operability: Operable
        Power State: On
        Thermal Status: OK
        Voltage Status: N/A

    PSU 4:
        Threshold Status: N/A
        Overall Status: N/A
        Operability: N/A
        Power State: Off
        Thermal Status: N/A
        Voltage Status: N/A

 

1 Accepted Solution

Accepted Solutions

On that version, most of the I2C issues have been fixed but if the chassis has been affected for a while, your I2C may have been congested for a while.

To clear the I2C bus, you need to reseat the components that use it... PSUs, Fans and IOMs so the recommendation would be to:

1-reseat each fan and PSU (one at the time and waiting 3 minutes before putting it back) once up again, proceed with the next one

2-Remove the subordinate IOM, keep it out of the chassis for about 5 mins to drain all power, put it back and wait until it comes back before proceeding with the other one.

 

Be sure you have network redundancy configured before doing this and if you need further assistance or dont feel comfortable with the process, contact TAC for further assistance.

If this helps, please rate it... if it solves the issue, please mark it as such for future users to take advantage of it too.

-Kenny         

View solution in original post

10 Replies 10

Keny Perez
Level 8
Level 8

We need to begin with the physical layer... did you reseat the power cables and PSUs already?  Have you changed the PSU's cable with one of the working PSUs to see if the issue is with the cables? (unlikely, but better rule it out).

 

Let me know if it doesnt help.

-Kenny

Yes I reseated PSU 2 & 4, I have also swapped cables from PSU 3 & 4 and even swapped PSU 1 & 4

Something appears to be looping maybe ...Here's some output from my FI:

 

cdcfi01-B /chassis # show psu detail

PSU:
    PSU: 1
    Overall Status: Operable
    Operability: Operable
    Threshold Status: OK
    Power State: On
    Presence: Equipped
    Thermal Status: OK
    Voltage Status: OK
    Product Name: Platinum II AC Power Supply for UCS 5108 Chassis
    PID: UCSB-PSU-2500ACDV
    VID: V01
    Part Number: 341-0571-01
    Vendor: Cisco Systems Inc
    Serial (SN): 
    HW Revision: 0
    Firmware Version: N/A

    PSU: 2
    Overall Status: Operable
    Operability: Operable
    Threshold Status: N/A
    Power State: On
    Presence: Equipped
    Thermal Status: N/A
    Voltage Status: N/A
    Product Name: Platinum II AC Power Supply for UCS 5108 Chassis
    PID: UCSB-PSU-2500ACDV
    VID: V01
    Part Number: 341-0571-01
    Vendor: Cisco Systems Inc
    Serial (SN): 
    HW Revision: 0
    Firmware Version: N/A

    PSU: 3
    Overall Status: Operable
    Operability: Operable
    Threshold Status: N/A
    Power State: On
    Presence: Equipped
    Thermal Status: OK
    Voltage Status: N/A
    Product Name: Platinum II AC Power Supply for UCS 5108 Chassis
    PID: UCSB-PSU-2500ACDV
    VID: V01
    Part Number: 341-0571-01
    Vendor: Cisco Systems Inc
    Serial (SN): 
    HW Revision: 0
    Firmware Version: N/A

    PSU: 4
    Overall Status: Operable
    Operability: Operable
    Threshold Status: N/A
    Power State: On
    Presence: Equipped
    Thermal Status: N/A
    Voltage Status: N/A
    Product Name: Platinum II AC Power Supply for UCS 5108 Chassis
    PID: UCSB-PSU-2500ACDV
    VID: V01
    Part Number: 341-0571-01
    Vendor: Cisco Systems Inc
    Serial (SN): 
    HW Revision: 0
    Firmware Version: N/A
cdcfi01-B /chassis # show psu

PSU:
    PSU        Overall Status
    ---------- --------------
             1 Operable
             2 N/A
             3 Operable
             4 N/A
cdcfi01-B /chassis # show psu detail
  <CR>
  >       Redirect it to a file
  >>      Redirect it to a file in append mode
  expand  Expand
  |       Pipe command output to filter


cdcfi01-B /chassis # show psu detail

PSU:
    PSU: 1
    Overall Status: Operable
    Operability: Operable
    Threshold Status: OK
    Power State: On
    Presence: Equipped
    Thermal Status: OK
    Voltage Status: OK
    Product Name: Platinum II AC Power Supply for UCS 5108 Chassis
    PID: UCSB-PSU-2500ACDV
    VID: V01
    Part Number: 341-0571-01
    Vendor: Cisco Systems Inc
    Serial (SN): 
    HW Revision: 0
    Firmware Version: N/A

    PSU: 2
    Overall Status: N/A
    Operability: N/A
    Threshold Status: N/A
    Power State: Off
    Presence: Equipped
    Thermal Status: N/A
    Voltage Status: N/A
    Product Name: Platinum II AC Power Supply for UCS 5108 Chassis
    PID: UCSB-PSU-2500ACDV
    VID: V01
    Part Number: 341-0571-01
    Vendor: Cisco Systems Inc
    Serial (SN): 
    HW Revision: 0
    Firmware Version: N/A

    PSU: 3
    Overall Status: Operable
    Operability: Operable
    Threshold Status: N/A
    Power State: On
    Presence: Equipped
    Thermal Status: OK
    Voltage Status: N/A
    Product Name: Platinum II AC Power Supply for UCS 5108 Chassis
    PID: UCSB-PSU-2500ACDV
    VID: V01
    Part Number: 341-0571-01
    Vendor: Cisco Systems Inc
    Serial (SN): 
    HW Revision: 0
    Firmware Version: N/A

    PSU: 4
    Overall Status: N/A
    Operability: N/A
    Threshold Status: N/A
    Power State: Off
    Presence: Equipped
    Thermal Status: N/A
    Voltage Status: N/A
    Product Name: Platinum II AC Power Supply for UCS 5108 Chassis
    PID: UCSB-PSU-2500ACDV
    VID: V01
    Part Number: 341-0571-01
    Vendor: Cisco Systems Inc
    Serial (SN): 
    HW Revision: 0
    Firmware Version: N/A
cdcfi01-B /chassis #
cdcfi01-B /chassis #

 

This is the first time I've caught status 'On' for PSU 2 & 4 via CLI

 

Do the following:

#connect local a

#connect iom <Chassis number>

#show platform software cmc power red

#show platform software cmc showi2c

#exit

#connect local b  >>>>> and repeat the commands above

 

What is the firmware version you are running?

-Kenny

Output attached

This seems to be a problem with the I2C bus, what firmware are you running?

 

cdcfi01-B# connect local-mgmt a

cdcfi01-A(local-mgmt)# connect iom 1
Attaching to FEX 1 ...
To exit type 'exit', to abort type '$.'
Bad terminal type: "dumb". Will assume vt100.
fex-1# show platform software cmcctrl po
post    power
fex-1# show platform software cmcctrl power redundancy
==============================
Cluster master                 : yes   <<< Primary IOM in the chassis
Policy                        : Grid
State                        : Lost  <<<< Not complaint with the power policy
Total power available        : 5000  <<<< 2 PSUs available
Total power usage        : 412
Power budget requested        : 5000
-----------
Grid                        : 0
        Active PS        : 0
        Spare PS        :
        Unavailable PS        : 1  <<<<<< PSU 2
-----------
-----------
Grid                        : 1
        Active PS        : 2      
        Spare PS        :
        Unavailable PS        : 3  <<<< PSU 4
-----------
==============================
fex-1#
fex-1# show platform software cmcctrl showi2c
# I2C Bus Statistics Wed Jun 17 09:46:56 CDT 2015
# I2C Bus 2
busn=1 nseg=5
segment 0 local
segment 1 chassis
        norxack 25
        pca9541seterr 32
        wait_gt_deadline 67
segment 2 blade
segment 3 fan
        norxack 333    <<< Not good
        wait_gt_deadline 22068
segment 4 psu
        norxack 766   <<<< not good
        pca9541clrerrprs 572   <<<< not good
        pca9541seterr 194
        wait_gt_deadline 20453
gilroy.error.pca9541_control_state 35
error_pca9541_per_device:
                c.ms 3
                p.psu3.psmi 52  <<<< PSU ERRORS
                p.psu0.ms 13    <<<< PSU ERRORS
                p.psu1.fru 54    <<<< PSU ERRORS
                p.psu1.ms 253    <<<< PSU ERRORS
                p.psu1.psmi 35   <<<< PSU ERRORS
                p.psu3.fru 53    <<<< PSU ERRORS
                p.psu3.ms 306   <<<< PSU ERRORS
                c.gpio0 8    <<< Chassis midplane errors
                c.gpio1 8
                c.gpio2 8
                c.gpio3 8

# I2C Device Statistics
p.psu0.psmi={SUCCESS=959191,EBUSY=1}    <<< BUSY signal from PSU when the IOM queries its status
p.psu1.fru={SUCCESS=2,ETIMEDOUT=9}      <<< Timeout signal from PSU2 when the IOM queries its status
p.psu3.fru={SUCCESS=2,ETIMEDOUT=8}      <<< Timeout signal from PSU4 when the IOM queries its status

*******************************************************************************************

cdcfi01-A(local-mgmt)# exit
cdcfi01-B# connect iom 1

fex-1# show platform software cmcctrl po
post    power
fex-1# show platform software cmcctrl power redundancy
==============================
Cluster master                 : no
Policy                        : Grid
State                        : Lost
Total power available        : 5000
Total power usage        : 414
Power budget requested        : 5000
-----------
Grid                        : 0
        Active PS        : 0
        Spare PS        :
        Unavailable PS        : 1
-----------
-----------
Grid                        : 1
        Active PS        : 2
        Spare PS        :
        Unavailable PS        : 3
-----------
==============================


fex-1# show platform software cmcctrl showi2c

# I2C Bus 2
busn=1 nseg=5
segment 0 local
segment 1 chassis
        norxack 52
        pca9541seterr 31
        wait_gt_deadline 61
segment 2 blade
segment 3 fan   <<< Clear, compared against the other IOM
segment 4 psu
        norxack 398    <<< Not good
        pca9541clrerrprs 268
        pca9541seterr 130
        wait_gt_deadline 12969
error_pca9541_per_device:
                c.ms 2
                p.psu3.psmi 42   <<< Not good
                p.psu0.ms 26     <<< Not good
                p.psu1.fru 30
                p.psu1.ms 119
                p.psu1.psmi 34
                p.psu3.fru 24
                p.psu3.ms 123
                c.gpio0 8
                c.gpio1 8
                c.gpio2 8
                c.gpio3 7

# I2C Device Statistics
p.psu1.fru={SUCCESS=5,ETIMEDOUT=5} <<< Timeout signal from PSU2 when the IOM queries its status
p.psu3.fru={SUCCESS=4,ETIMEDOUT=4}   <<< Timeout signal from PSU4 when the IOM queries its status

 

 

-Kenny

cdcfi01-B# sh version
System version: 2.2(3c)

 

On that version, most of the I2C issues have been fixed but if the chassis has been affected for a while, your I2C may have been congested for a while.

To clear the I2C bus, you need to reseat the components that use it... PSUs, Fans and IOMs so the recommendation would be to:

1-reseat each fan and PSU (one at the time and waiting 3 minutes before putting it back) once up again, proceed with the next one

2-Remove the subordinate IOM, keep it out of the chassis for about 5 mins to drain all power, put it back and wait until it comes back before proceeding with the other one.

 

Be sure you have network redundancy configured before doing this and if you need further assistance or dont feel comfortable with the process, contact TAC for further assistance.

If this helps, please rate it... if it solves the issue, please mark it as such for future users to take advantage of it too.

-Kenny         

Great, none of this gear is in production yet - we just racked/stacked a couple weeks ago. I'll proceed and report back -thanks for the help

robinsonjas
Level 1
Level 1

Thanks Kenny for the help....Since our gear wasn't even setup fully yet or running anything we just pulled power for 10minutes per chassis and it cleared the errors.

That was another way to go!   ;0)

Glad to help!

 

-Kenny